# LCN Binding
Local Control Network (LCN) (opens new window) is a building automation system. It is capable of controlling lights, shutters, access control etc. and can process data from several sensor types. It was introduced in 1992.
A broad range of glass key panels, displays, remote controls, sensors and in- and outputs exist. The system can handle up to 30,000 bus members, called modules. LCN modules are available for DIN rail and in-wall mounting and feature versatile interfaces. The bus modules and most of the accessories are developed, manufactured and assembled in Germany.
Bus members are inter-connected via a free wire in the standard NYM cable. Wireless components are available, though.
Illustration of the LCN product family
This binding uses TCP/IP to access the LCN bus via the software LCN-PCHK (Windows/Linux) or the DIN rail device LCN-VISU. This means 1 unused LCN-PCHK license or a LCN-VISU is required
# Thing: LCN Module
Any LCN module that should be controlled or visualized, need to be added to openHAB as a Thing.
LCN modules with firmware versions 120612 (2008), 170602 (2013) and 1F080A (2021) were tested with this binding. Modules with older and newer firmware should work, too. The module hardware types (e.g. LCN-SH, LCN-HU, LCN-UPP, ...) are compatible to each other and can therefore be handled all in the same way.
Thing Type ID: module
Name Description Type Required
moduleId The module ID, configured in LCN-PRO Integer Yes
segmentId The segment ID the module is in (0 if no segments are present) Integer Yes
openHAB's discovery function can be used to add LCN modules automatically. See Discover LCN Modules.
# Bridge: LCN PCK Gateway
PCK is the protocol spoken over TCP/IP with a PCK gateway to communicate with the LCN bus. Examples for PCK gateways are the LCN-PCHK software running on Windows or Linux and the DIN rail mounting device LCN-VISU.
For each LCN bus, interfaced to openHAB, a PCK gateway needs to be added to openHAB as a Thing.
Several PCK gateways can be added to openHAB to control multiple LCN busses in distinct locations.
The minimum recommended version is LCN-PCHK 3.3 (older versions will also work, but lack some functionality). Visit https://www.lcn.eu (opens new window) for updates.
Thing Type ID: pckGateway
hostname Hostname or IP address of the LCN-PCHK gateway String Yes
port TCP port of the LCN-PCHK gateway (default:4114) Integer Yes
username Username configured within LCN-PCHK Monitor String Yes
password Password configured within LCN-PCHK Monitor String Yes
mode Dimmer resolution: native50 or native200 See below. String Yes
timeoutMs Period after which an LCN command is resent, when no acknowledge has been received (in ms) (default: 3500) Integer Yes
ATTENTION: You must set the correct dimmer output resolution in the PCK Gateway Thing (mode)! This setting is crucial, and valid for the whole LCN bus.
It is either 0-50 steps or 0-200 steps. It has to be the same as in the parameterizing software LCN-PRO under Options/Settings/Expert Settings.
When using a wrong dimmer output setting, dimming the outputs will result in unintended behavior!
Please see the following LCN-PRO screenshot to determine the dimmer output resolution for the LCN bus:
LCN-PRO screenshot, showing the 50 or 200 steps for the dimmer outputs
# Thing: LCN Group
LCN modules can be assigned to groups with the programming software LCN-PRO.
To send commands to an LCN group, the group needs to be added to openHAB as a Thing.
One LCN module within the group is used to represent the status of the whole group. For example, when a Dimmer Output is controlled via a LCN group Thing, openHAB will always visualize the state of the Dimmer Output of the chosen module. The states of the other modules in the group are ignored for visualization.
Thing Type ID: group
groupId The group number, configured in LCN-PRO Integer Yes
moduleId The module ID of any module in the group. The state of this module is used for visualization of the group as representative for all modules. Integer Yes
segmentId The segment ID of all modules in this group (0 if no segments are present) Integer Yes
The groupId must match the previously configured group number in the programming software LCN-PRO.
# Discover LCN Modules
Basic data like the names of all LCN modules in the bus, can be read out by openHAB's discovery function.
If not all LCN modules get listed on the first run, click on the refresh button to start another scan.
When adding a module by discovery, the new Thing's UID will be a combination of segment and module id using the following format: S<segmentId>M<moduleId> where segmentId and moduleId are formatted as three-digit numbers with leading zeros.
# Discover PCK Gateways
PCK gateways in the LAN can be found automatically by openHAB. This is done by UDP multicast messages on port 4220. The discovery works only if the firewall of the PCK gateway is not configured too strictly. This means on Windows PCs, that the network must be configured as 'private' and not as 'public'. Also, some network switches may block multicast packets. Unfortunately, LCN-PCHK listens only on the first network interface of the computer for discovery packets. If your PCK gateway has multiple network interfaces, LCN-PCHK may listen on the wrong interface and fails to respond to the discovery request.
Discovery has successfully been tested with LCN-PCHK 3.2.2 running on a Raspberry Pi with Raspbian and openHAB running on Windows 10.
If discovery fails, you can add a PCK gateway manually. See Thing: PCK Gateway.
Please be aware that you have to configure username, password and the dimmer output resolution also if you use discovery. See Thing: PCK Gateway.
When adding a PCK gateway by discovery, the new Thing's UID is the MAC address of the device, running the PCK gateway.
# Supported LCN Features and openHAB Channels
The following table lists all features of LCN and their mappings to openHAB Channels. These Channels are available for the Thing LCN module (module). LCN group (group) has the same Channels, except status-only Channels like binary sensors or transponders. The PCK gateway (pckGateway) has no Channels.
Although, there are many Not implemented entries, the vast majority of LCN features can be used with openHAB:
If a special command is needed, the Hit Key action (German: "Sende Tasten") can be used to hit a module's key virtually and execute an arbitrary command.
LCN Feature (English) LCN Feature (German) Channel IDs Type Description
Dimmer Output Control Single Ausgang output 1-4 Dimmer, Switch Sets the dimming value of an output with a given ramp.
Dimmer Output Control Color Ausgang Farbe output color Color, Switch Sets the outputs 1-4 to control an RGBW lamp.
Tunable White Mode Tunable White Modus output tunablewhite String Sets the module's tunable white mode: DISABLE: Tunable white disabled. OUTPUT1: Output 1 is used for controlling. Output 2 is adjusted automatically. BOTH: Output 1 is used to control the brightness. Output 2 controls the temperature.
Relay Relais relay 1-8 Switch Controls a relay and visualizes its state.
Visualize Binary Sensor Binärsensor anzeigen binarysensor 1-8 Contact Visualizes the state of a binary sensor (special channel mapping for some devices).
LED Control LED-Steuerung led 1-12 String Controls an LED and visualizes its current state: ON, OFF, BLINK, FLICKER
Visualize Logic Operations Logik Funktion anzeigen logic 1-4 String Visualizes the result of the logic operation: NOT, OR, AND
Motor/Shutter on Dimmer Outputs Motor/Rollladen an Ausgängen rollershutteroutput 1-4 Rollershutter Control roller shutters on dimmer outputs
Motor/Shutter on Relays Motor/Rollladen an Relais rollershutterrelay 1-4 Rollershutter, Dimmer Control position of roller shutters on relays (Supports UpDown, StopMove, Percent)
Shutter Slat Angle on Relays Rollladenlamellen an Relais rollershutterrelayslat 1-4 Rollershutter, Dimmer Control slat angle of roller shutters on relays (Supports UpDown, StopMove, Percent)
Variables Variable anzeigen variable 1-12 Number Sets and visualizes the value of a variable. See note.
Regulator Set Setpoint Regler Sollwert ändern rvarsetpoint 1-2 Number Sets and visualizes the setpoint of a regulator.
Regulator Set Mode Reglerverhalten ändern rvarmode 1-2 String Sets the mode of the regulator: HEATING or COOLING
Regulator Lock Regler sperren rvarlock 1-2 Switch Locks a regulator and visualizes its locking state.
Set Thresholds in Register 1 Schwellwert in Register 1 ändern thresholdregister1 1-4 Number Sets and visualizes a threshold in the given threshold register.
Set Thresholds in Register 2 Schwellwert in Register 2 ändern thresholdregister2 1-4 Number Sets and visualizes a threshold in the given threshold register.
Set Thresholds in Register 3 Schwellwert in Register 3 ändern thresholdregister3 1-4 Number Sets and visualizes a threshold in the given threshold register.
Set Thresholds in Register 4 Schwellwert in Register 4 ändern thresholdregister4 1-4 Number Sets and visualizes a threshold in the given threshold register.
Visualize S0 Counters S0-Zähler anzeigen s0input 1-4 Number Visualizes the value of a S0 counter.
Lock Keys Table A Sperre Tastentabelle A keylocktablea 1-8 Switch Locks a key on the given key table and visualizes its state.
Lock Keys Table B Sperre Tastentabelle B keylocktableb 1-8 Switch Locks a key on the given key table and visualizes its state.
Lock Keys Table C Sperre Tastentabelle C keylocktablec 1-8 Switch Locks a key on the given key table and visualizes its state.
Lock Keys Table D Sperre Tastentabelle D keylocktabled 1-8 Switch Locks a key on the given key table and visualizes its state.
Dimmer Output Flicker Ausgang: Flackern N/A N/A N/A Action "flickerOutput": Let a dimmer output flicker for a given count of flashes.
Dynamic Text Dynamischer Text N/A N/A N/A Action: "sendDynamicText": Sends custom text to an LCN-GTxD display.
Send Keys Sende Tasten N/A N/A N/A Action: "hitKey": Hits a key of a key table in an LCN module. Can be used to execute commands, not supported by this binding.
Dimmer Output Control Multiple Mehrere Ausgänge steuern output 1-4 Dimmer, Switch Control multiple outputs simultaneously. See below.
Transponder Transponder code#transponder Trigger Receive transponder messages
Fingerprint Fingerprint code#fingerprint Trigger Receive fingerprint code messages
Remote Control Fernbedienung code#remotecontrolkey Trigger Receive commands from remote control
Access Control Zutrittskontrolle code#remotecontrolcode Trigger Receive serial numbers from remote control
Remote Control Battery Low Fernbedienung Batterie schwach code#remotecontrolbatterylow Trigger Triggered when the sending remote control has a low battery
Host Command (Send Keys) Kommando an Host (Sende Tasten) hostcommand#sendKeys - Trigger Receive send keys command from LCN module
Operating Hours Counter Outputs Betriebsstundenzähler Ausgänge operatinghourscounter output[1-4] Number:Time Visualize Operating Hours Counter for outputs
Operating Hours Counter Outputs (rel. Work) Betriebsstundenzähler Ausgänge (rel. Arbeit) operatinghourscounter outputrelativework[1-4] Number:Time Visualize Operating Hours Counter for outputs (relative work)
Operating Hours Counter Relays Betriebsstundenzähler Relais operatinghourscounter relay[1-8] Number:Time Visualize Operating Hours Counter for relays
Operating Hours Counter Binary Sensor Betriebsstundenzähler Binärsensoren operatinghourscounter binarysensor[1-8] Number:Time Visualize Operating Hours Counter for binary sensors
Status Message Statusmeldungen - - - Automatically done by openHAB Binding
Audio Beep Audio Piepen N/A N/A N/A Action: "beep" (see below)
Audio LCN-MRS Audio LCN-MRS - - - Not implemented
Count/Compute Zählen/Rechnen - - - Not implemented
DALI DALI - - - Not implemented
Dimmer Output Memory Toggle Ausgang: Memory Taster - - - Not implemented
Dimmer Output Ramp Stop Ausgang: Rampe Stop - - - Not implemented
Dimmer Output Relative Ausgang: Relativ - - - Not implemented
Dimmer Output Stairway Ausgang: Treppenhauslicht - - - Not implemented
Dimmer Output Timer Ausgang: Timer (Kurzzeit) - - - Not implemented
Display Set Language Display-Sprache setzen - - - Not implemented
Dynamic Groups Dynamische Gruppen - - - Not implemented
Free Input Freie Eingabe - - - Not implemented
LED Brightness LED-Helligkeit - - - Not implemented
LED Test LED-Test - - - Not implemented
LED Transform LED-Umwandlung - - - Not implemented
Light Scenes Lichtszenen - - - Not implemented
Lock Keys by Time (Table A) Sperre (Zeit) Tasten (Tabelle A) - - - Not implemented
Lock Outputs by Time Sperre (Zeit) Ausgänge - - - Not implemented
Lock Relays Sperre Relais - - - Not implemented
Lock Thresholds Sperre Schwellwerte - - - Not implemented
Motor Position Motor Position - - - Not implemented
Relay Timer Relais-Timer N/A N/A N/A Action: "startRelayTimer" (see below)
Send Keys Delayed Sende Tasten verzögert - - - Not implemented
Set S0 Counters S0-Zähler setzen - - - Not implemented
Status Command Statuskommandos - - - Not implemented
Notes:
  • For some _Channel_s (e.g. temperature) a unit should be configured in the channel configuration. By default the native LCN value is used.
  • S0 counter Channels need to be the pulses per kWh configured. If the value is left blank, a default value of 1000 pulses/kWh is set.
  • When setting a variable via openHAB, the variable must be configured as counter in LCN-PRO. The variable must be set initially by the module after power up.
  • The Rollershutter Channels provide the boolean parameter invertUpDown, which can be set to 'true' if the Up/Down wires are interchanged.
  • The binary sensor Channels provide the boolean parameter invertState, which can be set to 'true' if the binary sensor connected uses inverted logic for signaling open/closed.
# Transponder/Fingerprints
LCN transponder readers or fingerprint readers can be integrated in openHAB e.g. for access control. The transponder function must be enabled in the module's I-port properties within LCN-PRO.
Example: When the transponder card with the ID "12ABCD" is seen by the reader connected to LCN module "S000M011", the item "M10_Relay7" is switched on:
rule "My Transponder"
    Channel "lcn:module:b827ebfea4bb:S000M011:code#transponder" triggered "12ABCD"
    M10_Relay7.sendCommand(ON)
Example: When fingerprint with ID "AFFE12" is seen by reader connected to LCN module "S000M011", the item "M10_Relay7" is switched on:
rule "My Fingerprint"
    Channel "lcn:module:b827ebfea4bb:S000M011:code#fingerprint" triggered "AFFE12"
# Command from an LCN Module to openHAB
LCN modules can send commands to openHAB, e.g. by pressing a physical LCN key. The command must be programmed into the LCN module by the programming software LCN-PRO. Only the send keys command (German: "Sende Tasten") is supported.
Program a command to a key of an LCN module via LCN-PRO. When LCN-PRO asks you for the target address, don't select any module, but manually enter the PCK host ID, configured within PCHK (default: 4). Select the send keys command and "A-C (former command)", as PCHK 3.2.2 only supports the old command. Then, select any key(s) you want to send to openHAB. These can be freely chosen, as they are only evaluated by openHAB.
Screenshot, showing the send keys command
The following rule can be used to trigger any action:
rule "Module 12 sent A1 Hit"
    Channel "lcn:module:b827ebfea4bb:S000M012:hostcommand#sendKeys" triggered "A1:HIT"
A1 is the key of the send keys command, programmed by LCN-PRO. After the colon, the LCN "hit type" follows: HIT, MAKE or BREAK (German: kurz, lang, los)
If multiple keys or key tables are programmed in a single "send keys" command, multiple triggers will be executed.
Notice: Don't test the command with the "Test command" button in LCN-PRO. This will send a command from LCN-PRO to openHAB, but openHAB expects the module as the sender. Simply press the physical button at the module for testing.
# Remote Control
To evaluate commands from LCN remote controls (e.g. LCN-RT or LCN-RT16), the module's I-port behavior must be configured as "IR access control" within LCN-PRO:
Screenshot, showing the I-port properties for remote controls
# Remote Control Keys
The trigger Channel lcn:module:<pckThing>:<moduleThing>:code#remotecontrolkey can be used to execute commands, when a specific key on a remote control is pressed:
rule "Remote Control Key 3 on Layer 1 hit"
    Channel "lcn:module:b827ebfea4bb:S000M012:code#remotecontrolkey" triggered "A3:HIT"
A3 is key 3 on the first layer. B1 is key 1 on the second layer etc.. After the colon follows the LCN "hit type" HIT, MAKE or BREAK (German: kurz, lang, los).
# Remote Control used as Access Control
The serial number of a remote control can be used for access control via the channel lcn:module:<pckThing>:<moduleThing>:code#remotecontrolcode. See the following example:
rule "Remote Control Key 3 on Layer 1 hit (only executed for serial number AB1234)"
    Channel "lcn:module:b827ebfea4bb:S000M012:code#remotecontrolcode" triggered "AB1234:A3:HIT" or
    Channel "lcn:module:b827ebfea4bb:S000M012:code#remotecontrolcode" triggered "AB1234:A3:MAKE"
The command will be executed when the remote control button A3 is either pressed short or long.
# Dimmer Outputs with Ramp and Multiple Outputs
The output profile can be used to control multiple dimmer outputs of the same module simultaneously or control a dimmer output with a ramp (slowly dimming).
The optional ramp parameter must be float or integer. The lowest value is 0.25, which corresponds to 0.25s. The highest value is 486s. When no ramp parameter is specified or no profile is configured, the ramp is 0 (behavior like a switch). The ramp parameter is not available for Color _Item_s.
// Dim output 2 in 0.25s
Switch M10_Output2 {channel="lcn:module:b827ebfea4bb:S000M010:output#2"[profile="lcn:output", ramp=0.25]} // with ramp of 0.25s (smallest value)
// Dim output 3 in 486s
Dimmer M10_Output3 {channel="lcn:module:b827ebfea4bb:S000M010:output#3"[profile="lcn:output", ramp=486]}  // with ramp of 486s (biggest value)
The optional parameters controlAllOutputs and controlOutputs12 can be used to control multiple outputs simultaneously. Please note that the combination of these parameters with the ramp parameter is limited:
// Control outputs 1+2 simultaneously. Status of Output 1 is visualized. Only ramps of 0s or 0.25s are supported.
Dimmer M10_Outputs12a {channel="lcn:module:b827ebfea4bb:S000M010:output#1"[profile="lcn:output", controlOutputs12=true]}
Dimmer M10_Outputs12b {channel="lcn:module:b827ebfea4bb:S000M010:output#1"[profile="lcn:output", controlOutputs12=true, ramp=0.25]}
// Control all outputs simultaneously. Status of Output 1 is visualized.
Dimmer M10_OutputAll1 {channel="lcn:module:b827ebfea4bb:S000M010:output#1"[profile="lcn:output", controlAllOutputs=true, ramp=0]} // ramp only since firmware 180501
Dimmer M10_OutputAll2 {channel="lcn:module:b827ebfea4bb:S000M010:output#1"[profile="lcn:output", controlAllOutputs=true, ramp=0.25]} // ramp compatibility: all
Dimmer M10_OutputAll3 {channel="lcn:module:b827ebfea4bb:S000M010:output#1"[profile="lcn:output", controlAllOutputs=true, ramp=0.5]} // ramp only since firmware 180501
Actions are special commands that can be sent to LCN modules or LCN groups.
# Hit Key
This Action virtually hits a key of a key table in an LCN module. Simply spoken, openHAB acts as a push button switch connected to an LCN module.
This Action can be used to execute commands which are not natively supported by this binding. The function can be programmed via the software LCN-PRO onto a key in a module's key table. Then, the programmed key can be "hit" by this Action and the command will be executed.
When programming a "Hit Key" Action, the following parameters need to be set:
table - The module's key table: A, B, C or D
key - The number of the key within the key table: 1-8
action - The key's action: HIT (German: "kurz"), MAKE ("lang") or BREAK ("los")
rule "Hit key C4 hourly"
    Time cron "0 0 * * * ?"
    val actions = getActions("lcn","lcn:module:b827ebfea4bb:S000M010")
    actions.hitKey("C", 4, "HIT")
# Dynamic Text
This Action can be used to send custom texts to an LCN-GTxD display. To make this function work, the row of the display has to be configured to allow dynamic text within LCN-PRO:
Screenshot of LCN-PRO, showing the dynamic text setting of an LCN-GT10D
When programming a "Dynamic Text" Action, the following parameters need to be set:
row - The number of the row in the display: 1-4
text - The text to be displayed (UTF-8)
The length of the text may not exceed 60 bytes of characters. Bear in mind that unicode characters can take more than one byte (e.g. umlauts (äöü) take two bytes).
rule "Send dynamic Text to GT10D hourly"
    val actions = getActions("lcn","lcn:module:b827ebfea4bb:S000M012")
    actions.sendDynamicText(1, "Test 123 CO₂ öäü߀") // row 1
# Flicker Output
This Action realizes the LCN command "Output: Flicker" (German: "Ausgang: Flackern"). The command let a dimmer output flash a given number of times. This feature can be used e.g. for alert signals or visual door bells.
When programming a "Flicker Output" Action, the following parameters need to be set:
output - The dimmer output number: 1-4
depth - The depth of the flickering: 0-2 (0=25% 1=50% 2=100% Example: When the output is fully on (100%), and 0 is selected, flashes will dim from 100% to 75% and back)
ramp - The duration/ramp of one flash: 0-2 (0=2sec 1=1sec 2=0.5sec)
count - The number of flashes: 1-15
This action has also effect, if the given output is off. The output will be dimmed from 0% to depth and back, then.
rule "Flicker output 1 when window opens"
    Item M10_BinarySensor5 changed to OPEN
    // output=1, depth=2=100%, ramp=0=2s, count=3
    actions.flickerOutput(1, 2, 0, 3)
# Relay Timer
This Action realizes the LCN commmand "Relay Timer" (German: "Relais-Timer"). The command switches the given relay immediately to on and after a given time back to off.
When programming a "Relay Timer" Action, the following parameters need to be set:
relayNumber - The relay number: 1-8
duration - Timer duration in milliseconds: 30-240.000 ms
rule "Start relay timer for led driver when dummy switch changed"
    Item Dummy_Switch changed
    val actions = getActions("lcn","lcn:module:b827ebfea4bb:17B4196847")
    // relayNumber=3, duration=90
    actions.startRelayTimer(3, 90)
# Beep
This Action realizes the LCN commmand "audio" (German: "Piepen"). It lets the beeper connected to the LCN module beep.
When programming an "audio" Action, the following parameters can be set:
volume - Sound volume in percent (if null, the previous volume will be used)
tonality - The tonality as a String. You need to use quotes. See below.
count - Number of beeps (max. 50)
Tonalities:
  • "N"=push button hit (normal)
  • "S"=special
  • "1"=push button make
  • "2"=push button break
  • "3"=standard
  • "4"=special
  • "5"=special short
  • "6"=error
  • "7"=long
rule "Beep when dummy switch changed"
    val actions = getActions("lcn","lcn:module:b827ebfea4bb:b0b029b920")
    // volume=100, tonality="6", count=2
    actions.beep(100, "6", 2)
# Caveat and Limitations
LCN segments are supported by this binding, but could not be tested, due to lack of hardware.
LEDs do not support the OnOffCommand and respectively the Switch Item type, because they have the additional states BLINK and FLICKER. They must be configured as String Item. When used in rules, the parameter must be of type string. Example: M10_LED1.sendCommand("ON"). Note the quotation marks.
Config .things
Bridge lcn:pckGateway:myPCHK [ hostname="192.168.123.123", port=4114, username="myUser", password="myPassword", mode="native200" ] {
 Thing module M99 "M99 MyModule" [ moduleId=99, segmentId=0 ] {
        Rollershutter : rollershutterrelay#1 "My twisted rollershutter relay" [ invertUpDown = true ]
  Contact : binarysensor#6 [ invertState=true ]
  Number  : rvarsetpoint#1 [ unit="temperature" ]
  Number  : variable#3     [ unit="temperature" ]
Config .items
// Dimmer Outputs
Dimmer M10_Output1 {channel="lcn:module:b827ebfea4bb:S000M010:output#1"}
// Dimmer Outputs: Control all simultaneously. Status of Output 1 is visualized.
Dimmer M10_OutputAll1 {channel="lcn:module:b827ebfea4bb:S000M010:output#1"[profile="lcn:output", controlAllOutputs=true, ramp=0]}    // ramp=0: only since firmware 180501
Dimmer M10_OutputAll2 {channel="lcn:module:b827ebfea4bb:S000M010:output#1"[profile="lcn:output", controlAllOutputs=true, ramp=0.25]} // ramp=0.25: compatibility: all firmwares
Dimmer M10_OutputAll3 {channel="lcn:module:b827ebfea4bb:S000M010:output#1"[profile="lcn:output", controlAllOutputs=true, ramp=0.5]}  // ramp>=0.5: only since firmware 180501
// Dimmer Outputs: Control outputs 1+2 simultaneously. Status of Output 1 is visualized. Only ramps of 0s or 0.25s are supported.
// Dimmer Outputs: RGB Control
Color M10_Color {channel="lcn:module:b827ebfea4bb:S000M010:output#color"[profile="lcn:output"]}
// Roller Shutter on Output 1+2
Rollershutter M10_RollershutterOutput1 {channel="lcn:module:b827ebfea4bb:S000M010:rollershutteroutput#1"}
// Relays
Switch M10_Relay1 {channel="lcn:module:b827ebfea4bb:S000M010:relay#1"}
// Roller Shutter on Relays 1+2
Rollershutter M10_RollershutterRelay1 {channel="lcn:module:b827ebfea4bb:S000M010:rollershutterrelay#1"}
Dimmer M10_RollershutterRelay1Slats {channel="lcn:module:68b8462b:S000M012:rollershutterrelayslat#1"}
// LEDs
String M10_LED1 {channel="lcn:module:b827ebfea4bb:S000M010:led#1"}
String M10_LED2 {channel="lcn:module:b827ebfea4bb:S000M010:led#2"}
// Logic Operations (legacy name: "Sums")
String M10_Logic1 {channel="lcn:module:b827ebfea4bb:S000M010:logic#1"}
String M10_Logic2 {channel="lcn:module:b827ebfea4bb:S000M010:logic#2"[profile="transform:MAP", function="alertSystem.map"]}
// conf/transform/alertSystem.map:
// NOT=All windows are closed
// OR=Some windows are open
// AND=All windows are open
// Binary Sensors (Channels 1-3 of LCN-B3I are mapped to BinarySensor6, BinarySensor7, BinarySensor8)
Contact M10_BinarySensor1 {channel="lcn:module:b827ebfea4bb:S000M010:binarysensor#1"}
// Variables
// The units of the variables must also be set in the Channels configuration, to be visualized correctly.
Number:Temperature M10_Variable1 "[%.1f %unit%]" <temperature> {channel="lcn:module:b827ebfea4bb:S000M010:variable#1"} // Temperature in °C
Number:Temperature M10_Variable2 "[%.1f °F]" <temperature> {channel="lcn:module:b827ebfea4bb:S000M010:variable#2"} // Temperature in °F
Number M10_Variable3 "[%d ppm]" <temperature> {channel="lcn:module:b827ebfea4bb:S000M010:variable#3"}              // Indoor air quality in ppm
Number M10_Variable4 "[%d lx]"    {channel="lcn:module:b827ebfea4bb:S000M010:variable#4"}                          // Illuminance in Lux
Number:Illuminance M10_Variable5 "[%.1f klx]" {channel="lcn:module:b827ebfea4bb:S000M010:variable#5"}              // Illuminance in kLux
Number M10_Variable6 "[%.1f mA]"  {channel="lcn:module:b827ebfea4bb:S000M010:variable#6"}                          // Electrical current in mA
Number M10_Variable7 "[%.1f V]"   {channel="lcn:module:b827ebfea4bb:S000M010:variable#7"}                          // Voltage in V
Number M10_Variable8 "[%.1f m/s]" {channel="lcn:module:b827ebfea4bb:S000M010:variable#8"}                          // Wind speed in m/s
Number M10_Variable9 "[%.1f °]"  {channel="lcn:module:b827ebfea4bb:S000M010:variable#9"}                           // position of the sun (azimuth or elevation) in °
Number M10_Variable10 "[%d W]"    {channel="lcn:module:b827ebfea4bb:S000M010:variable#10"}                         // Current power of an S0 input in W
Number:Power M10_Variable11 "[%.1f kW]" {channel="lcn:module:b827ebfea4bb:S000M010:variable#11"}                   // Current power of an S0 input in kW
// Regulators
Number:Temperature M10_R1VarSetpoint "[%.1f %unit%]" <temperature> {channel="lcn:module:b827ebfea4bb:S000M010:rvarsetpoint#1"} // Temperature in °C
Switch M10_R1VarLock {channel="lcn:module:b827ebfea4bb:S000M010:rvarlock#1"} // Lock state of R1Var
// Thresholds
Number:Temperature M10_ThresholdRegister1_Threshold1 "[%.1f %unit%]" {channel="lcn:module:b827ebfea4bb:S000M010:thresholdregister1#1"} // Temperature in °C
Number:Temperature M10_ThresholdRegister4_Threshold2 "[%.1f %unit%]" {channel="lcn:module:b827ebfea4bb:S000M010:thresholdregister4#2"} // Temperature in °C
// S0 Counters
Number:Energy M10_S0Counter1 "[%.1f kWh]" {channel="lcn:module:b827ebfea4bb:S000M010:s0input#1"}
// Key Locks
Switch M10_KeyLockA1 {channel="lcn:module:b827ebfea4bb:S000M010:keylocktablea#1"}
Switch M10_KeyLockD5 {channel="lcn:module:b827ebfea4bb:S000M010:keylocktabled#5"}
Config .sitemap
sitemap lcn label="My home automation" {
    Frame label="Demo Items" {
        // Dimmer Outputs
        Default item=M10_Output1 label="Output 1"
        Default item=M10_Output2 label="Output 2"
        Default item=M10_Output3 label="Output 3"
        Default item=M10_OutputAll1 label="All Outputs ramp=0 since firmware 180501"
        Default item=M10_OutputAll2 label="All Outputs ramp=250ms all firmwares"
        Default item=M10_OutputAll3 label="All Outputs ramp>=500ms since firmware 180501"
        Default item=M10_Outputs12a label="Outputs 1+2 Ramp=0"
        Default item=M10_Outputs12b label="Outputs 1+2 Ramp=0.25s"
        Colorpicker item=M10_Color
        // Roller Shutter on Outputs 1+2
        Default item=M10_RollershutterOutput1 label="Roller Shutter on Output 1+2"
        // Relays
        Default item=M10_Relay1 label="Relay 1"
        Default item=M10_RollershutterRelay1 label="Roller Shutter on Relay 1-2"
        Dimmer item=M10_RollershutterRelay1 label="Roller Shutter Position on Relay 1-2"
        Default item=M10_RollershutterRelay1Slats label="Roller Shutter Slat Angle on Relay 1-2"
        // LEDs
        Switch item=M10_LED1 label="LED 1" mappings=[ON=ON, OFF=OFF] // Don't display "Blink" or "Flicker"
        Switch item=M10_LED2 label="LED 2"
        Default item=M10_Logic1 label="Logic Operation 1"
        Default item=M10_Logic2 label="Logic Operation 2"
        Default item=M10_BinarySensor1 label="Binary Sensor 1"
        // Variables
        Setpoint item=M10_Variable1 label="Variable 1"
        Default item=M10_Variable2 label="Variable 2"
        Default item=M10_Variable3 label="Variable 3"
        Default item=M10_Variable4 label="Variable 4"
        Default item=M10_Variable5 label="Variable 5"
        Default item=M10_Variable6 label="Variable 6"
        Default item=M10_Variable7 label="Variable 7"
        Default item=M10_Variable8 label="Variable 8"
        Default item=M10_Variable9 label="Variable 9"
        Default item=M10_Variable10 label="Variable 10"
        Default item=M10_Variable11 label="Variable 11"
        // Regulators
        Setpoint item=M10_R1VarSetpoint label="R1Var Setpoint" step=1 minValue=-10.0
        Default item=M10_R1VarLock label="R1Var Lock"  // Lock state of R1Var
        // Thresholds
        Setpoint item=M10_ThresholdRegister1_Threshold1 label="Threshold Register 1 Threshold 1"
        Setpoint item=M10_ThresholdRegister4_Threshold2 label="Threshold Register 4 Threshold 2"
        // S0 Counters
        Default item=M10_S0Counter1 label="S0 Counter 1"
        // Key Locks
        Default item=M10_KeyLockA1 label="Locked State Key A1"
        Default item=M10_KeyLockD5 label="Locked State Key D5"